For a fuel oil burner installed in an enclosure, the burner is rated at 1.25 gph. What is the free area needed for each of the two required combustion air openings?

Prepare for the HVAC D-2 License Exam. Study with flashcards and multiple-choice questions. Each question comes with hints and explanations. Get ready for your HVAC certification!

Multiple Choice

For a fuel oil burner installed in an enclosure, the burner is rated at 1.25 gph. What is the free area needed for each of the two required combustion air openings?

Explanation:
Air for combustion must be sized to match the burner’s energy input. The rule is that each opening provides 1 square inch of free area for every 1,000 Btu/h of input. Convert the burner rating to Btu/h: 1.25 gallons per hour × about 140,000 Btu/gal ≈ 175,000 Btu/h. Divide by 1,000 to get the required free area per opening: 175,000 / 1,000 = 175 in². Since there are two openings, each needs 175 square inches of free area.

Air for combustion must be sized to match the burner’s energy input. The rule is that each opening provides 1 square inch of free area for every 1,000 Btu/h of input. Convert the burner rating to Btu/h: 1.25 gallons per hour × about 140,000 Btu/gal ≈ 175,000 Btu/h. Divide by 1,000 to get the required free area per opening: 175,000 / 1,000 = 175 in². Since there are two openings, each needs 175 square inches of free area.